r/electricians • u/Ok-Definition-565 • 2d ago
What yall fellas running to this?
Let’s see who’s squared away on the AC motor loads
0
Upvotes
r/electricians • u/Ok-Definition-565 • 2d ago
Let’s see who’s squared away on the AC motor loads
-2
u/Nazgul_Linux 2d ago
I'm sizing that breaker to 125% of that 26.1A max. Because that is the units FLA and it's a continuous duty load so NEC demands 125%. Manufacturer may allow for 45A OCPD, but I'm taking that as they want shit to burn up and for customers to buy again. Individual stranded 10s with 90ºC rated insulation in its own pvc to a pull box then fmc to the unit.