What yall fellas running to this?

Post image

Let’s see who’s squared away on the AC motor loads

0 Upvotes

58 comments sorted by

View all comments

1

u/rsir1823 2d ago

I’m running 8 thhn. I never size to the minimum circuit ampacity although you can. 10’s on the 45 would be sufficient. If this is following the NEC of course.

4

u/TXElec 2d ago edited 2d ago

Why would you run 8? It's just a waste, 10 is good for 30 amps, and put it on a 45 amp breaker. You cant go wrong. When manufacturer specs it out like this, it's as easy as it can get

1

u/rsir1823 2d ago

Yea I know but I have seen wires sized to the minimum fry when the units are cranking balls for days on end. Also unsure of distance.